Hello everyone, I'm new here, have a few questions about calculation methodology I guess, rather than number crunching.
So, we have this Type 2B 480V Magnum DS switchgear by Eaton with a main and a few feeder breakers. As you all know Type 2B offers protection around the entire perimeter with all doors closed and latched.
In the event of an arcing fault anywhere in the gear, the barriers between cells may (but not necessarily will) burn through so that theoretically the maximum arc energy, which in this case happens to be at the main incoming compartment due to the upstream device setting, is available anywhere within the gear.
My questions are:
- Do you assign this maximum energy to the entire lineup? Or
- For feeder breaker labels you take the energy available on the main bus (as protected by the main breaker)?
- Do you consider an arcing fault in the main incoming compartment and an open feeder breaker door a double contingency whose probability is remote?
Thanks,
I'd be happy to provide further clarifications if need be.