Hi,
i found in Etap software that are indicated the Category with reference to NFPA 2012.
Is this real?
Which is the last updated Standard on this matters?
PostPosted: Thu Jan 09, 2014 12:16 am
Do you mean the latest NFPA® 70E?
Or do you mean that there should be newer standards on this matter?
In the first case I have the ‘NFPA® 70E Standard for Electrical Safety in the Workplace 2012 Edition’ in 130.5 B they talk about arc flash PPE and refer to Annex D and Annex H.
In 130.7 there are a few tables with clothing split in Hazard/Risk category 0, 1, 2, 3 and 4.
PostPosted: Mon Jan 13, 2014 8:55 am
2012 is the latest edition. The new one will be 2015 and should be out by Sept/Oct 2014.