RECS wrote:
I am reviewing a project that is choosing to print in the labels the worst case incident energy from two calculations methods. IEEE or the NFPA Ralfph Lee equations. Whichever result is higher, that is the value going to the label.
This feels very wrong to me and I would never mixed these two calculation methods. The question is:
How can I argue using the NFPA 70E 2012 or IEEE standards that this mixing of methods is inadequate?
Thanks.
There are actually several methods:
IEEE 1584
"NFPA" which is based on a 2007 paper that preceded IEEE 1584
Ralph Lee's Method
Arc Pro or Heat Flux (software for systems > 15 kV)
IEEE 1584 is used almost exclusively for three phase arc flash up to 15 kV. It is based on the latest and greatest. (almost - we are working on the next generation of equations right now)
Above 15 kV a method other than IEEE 1584 should be used which is either Ralph Lee Equations, Arc Pro or Duke Heat Flux (software). The problem with the Lee method is although it was great back in the day (several decades ago), it is very theoretical and gives extremely high results as voltage increases. Most people would use Arc Pro or a similar program in this case.
If I understand what you are saying i.e. they are choosing the larger of IEEE 1584 or Ralph Lee results, I would question the capability of the person performing the study because this is all pretty common knowledge for people that have performed studies before.
Good Luck!