It is currently Tue Oct 13, 2026 9:29 pm
Would you be comfortable stating your company/client's electrical system is properly installed?
Yes 61%  61%  [ 23 ]
No 39%  39%  [ 15 ]
Total votes : 38
 Post subject: 2015 NFPA 70E and "The equipment is properly installed"
PostPosted: Sat Mar 29, 2014 7:36 pm
This week we continue the series of questions regarding "Normal Operation" as defined by the proposed 2015 Edition of NFPA 70E.
Another condition that must be satisfied is item (1) The equipment is properly installed.
130.2(4) Normal Operation.Normal operation of electric equipment shall be permitted where all of the following conditions are satisfied:(1) The equipment is properly installed.
An informational note follows that states:
...The phrase "properly installed" means that the equipment is installed in accordance with applicable industry codes and standards and the manufacturer's recommendations. industry codes and standards."
Here is this week's question:
Based on NFPA 70E's specific text, would you be comfortable stating that your company/client's electrical equipment is properly installed?
  • Yes
  • No
PostPosted: Thu Apr 03, 2014 6:36 am
I see this week's question about properly installed leans a lot more towards "yes" than last week regarding maintenance. Do most believe it might be because the burden (for properly installed) is less on the owner and more on the contractor/designer? Just thought I would throw that out there.
PostPosted: Thu Apr 03, 2014 7:22 am
My guess is that it's something (install) you do once, while maintenance is "forever after".
Install is usually more planned, while maintenance is "until it breaks".
It's more difficult to cut costs at installation if you need to install something, while maintenance gets cut easily.
PostPosted: Thu Apr 03, 2014 7:46 am
New installation involves months if not years of plannings and investment of dollars. Drawings are created and reviewed by independent teams. Scope of works are created from the drawings and reviewed by affected parties. Alternatives are evaluated, drawings are re done, scopes are tweaked. finally bids are let. A project/construction manager compare the work done to the scope, variances are addressed. Finally everything goes on-line.
Maintenance often involves just giving someone a screwdriver and a wrench and telling them to get production back up as fast as possible.
PostPosted: Thu Apr 03, 2014 10:16 am
One thing I have seen everywhere I have worked, though, is that maintenance will "reinstall" things to a much different standard than the original installation. Where I am right now I'm running into issues such as motors, as one example, that were upsized without the associated starters, overloads, and cables being changed as well. I've also frequently run into circumstances where I have documentation for the initial industrial plant, but very little documentation for the various upgrades, additions and subtractions that have been done through the years.
PostPosted: Thu Apr 03, 2014 12:58 pm
We have very good standards such as NEC for installation requirements. I can pretty easily demonstrate compliance with that document. Not so for maintenance.
This is similar to various "safety inspections". It is very simple to inspect things, but much harder to inspect activities.
