elihuiv wrote:
I'm glad OSHA did the research to show that IEEE 1584 should not be used on 15kV and above instead of what everyone had done up until this point, which was just extrapolate IEEE 1584 into infinity.
I disagree partly here. What IEEE 1584 doees is present at least three models for arc flash estimates, not just a single model. This would be missed if you don't have a copy of the actual standard. The first model, a theroetical one, is the Lee model. The second model, and the only one that for some reason the standard gets credit for, is the empirical model. The third model is a group of models that are very simple in nature but attempt to estimate incident energy from current limiting fuses. IEEE 1584 itself only makes a numerical argument for the accuracy of any of the models with regards to the empirical one.
Thus to say that most practitioners are "extrapolating IEEE 1584 into infinity" and especially with reference to software packages, that's just not true. ETAP, EasyPower and SKM switch to the Lee model when it deviates outside the stated boundaries of IEEE 1584. If you simply read the results, you'd miss this but at least in SKM (the one I use), it pops up a footnote that explains this.
I'm happy for one with what OSHA did. Let's say for instance that you are an engineer at say a large mining facility with a cogen that has internal distribution systems well over 15 kV. So the company gets the "arc flash bug". Now what? Well, we could appeal to the tables in 70E for this one case. Oh wait, as of 2015 any reference above 15 kV is deleted. So then we've got to find an alternative. My arc flash software prodcues a "result" but it is nonsensical (Lee) and I know it, and the results are patently ridiculous requiring 150+ cal/cm^2 suits in the main sub just because of the voltage. So what can I use? I could use NESC at least for open wire but what about the indoor, enclosed stuff? And if I just use a commercial software program (ArcPro) what justification do I use compared to Lee other than an appeal to sanity? And even failing all that, what if the worst happens and someone gets hurt and the company gets sued, and this issue comes up? I can hardly say that I'm following recommended practices from anyone, anywhere. Worse still, what if I'm an engineer at a small local REA utility and I've never even heard of this before and need to get up to speed quickly, and the local engineering firm is telling me that my guys have to dress in 100 cal suits and use 35 foot long hot sticks even to operate a recloser handle? What then? And yes, Lee really is that silly and that bad.
So, I am in agreement.
So lets say that a competitor to ArcPro comes along. Then what? Any competitor is really going to have to prove their results. That means comparisons to ArcPro, Lee, Duke heat flux, and hopefully real, measured data. Frankly, the fact that OSHA published this in an annex changes NOTHING. The same burden of proof is still required to use Brand B. This is much different from placing it in the text!
Finally as to the for-profit vs. the not-for-profit argument, what exactly is OSHA supposed to do, or anyone for that matter? Prior to the annex, we had a table of values in the NESC that descended from a mystery source that we can't talk about, or go out on your own and do the same analysis. Had OSHA put together the same table and simply labelled it as "Lee theoretical model", "Brand X" (Duke), and "Brand Y" (ArcPro), we'd be stuck at the same situation. Without know who brand X and Y are, it's just a meaningless comparison that can at best show how similar the results are and not for the purposes of software selection. ArcPro at least claims (although if you get the actual papers you will realize the information is incomplete) to be based on peer reviewed models. Duke heat flux is a lot more vague than that.
For that matter, IEEE 1584 empirical model is just that, a curve fit. There is ZERO theory behind it beyond statistical analysis. Yet we appeal to the empircal model as if it's the holy grail and reject alternatives which may be based on physics based on how well they compare to IEEE 1584, rather than to the underlying data. We have erected a substantial hurdle in the research space for even a 480 V arc flash model.