 Post subject: Regenerative Drive Contributions to Upstream Fault
PostPosted: Wed Nov 16, 2016 2:43 pm 

Joined: Tue Apr 17, 2012 9:17 am
Posts: 12
Is there any information on what a regenerative drive will allow a motor to contribute to an upstream fault? I know ANSI has some standards for motor contributions based on <50HP or >50HP for across the line starters. We have some DC motors with regen drives connected to a 480VAC system and I want to model the contributions of the motors on the upstream switchgear. A few of these motors are 500HP or bigger.

We used to use Easypower and I remember that had an option for selecting if your drive was Regen or Non-Regen, and that would affect the contributions. But the contributions of a regen drive was less than across-the-line for the same size motor.

We've since switched to etap, and their drive model doesn't have a re-gen option. Not to mention they don't have a real clean way to model a DC drive on an AC system.

I'm thinking there's a way I can model the load and the short circuit calculations if there's some sort of impedance multiplier for re-gen drives for the 1/2 cycle or 5 cycle short circuit.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Regenerative Drive Contributions to Upstream Fault
PostPosted: Fri Feb 10, 2017 2:41 am 

Joined: Thu Apr 02, 2015 11:39 pm
Posts: 2
Location: New Jersey
Sorry, but why did you switch to ETAP???


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Regenerative Drive Contributions to Upstream Fault
PostPosted: Sat Feb 11, 2017 10:58 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
Look in the information on the drive. They will give you a maximum current draw. Worst case, the transistors are rated for RMS ratings so they can't exceed approximately 200% of their maximum name plate ratings or the transistors turn into very fast fuses (blow up).


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883