wilhendrix wrote:
Paul, so you've done a few site specific PPE plans where you print labels and specify the exact PPE to wear?
I have been to plants that do this but I don't recommend it for two reasons. NFPA 70E has altered the list a couple times already for instance with getting rid of 2* and changing the face shield and balaclava requirements. Plus as the PPE supplier and/or PPE changes in house, you don't want to spend all your time running around reprinting labels. In addition when contractors come onto the site, their PPE requirements may not exactly match the site PPE.
So there are really only two options in my mind. The first is to simply put the incident energy on the label and be done with it. The second is to put that number on there but to "round up" to the plan specific PPE values as a way of "simplifying" things. That works as well as using your own levels but serves the dual purpose of supporting outside contractors or PPE changes/upgrades.
And as per my previous post, you CAN have a 4 or 5 level system but most plants only use 2 or 3 of them. It's really not that hard to figure out or memorize for anyone.