hi there. new member, first post. happy to find this forum.
have any of you ever heard of anything like this?
- techs were working to pull in new cable feeds with grounds into an MCC (MCC1).
- system config is as follows: source is an old 480V switchgear with drawout breakers feeding various 480V mccs. one of these breakers (call it oldmain) feeds MCC1 temporarily until a new 480v swgr can be installed.
- the new cables being pulled in are the new source cable from the new 480V switchgear.
- oldmain is opened up, locked out, but not racked off the bus.
- mcc1 main breaker (call it mccmain) is turned off. 4 hours later, cable pull work commences.
- the copper ground wire inadvertently makes contact with A-phase primary lug of mccmain, and theres a spark.
- tech is working right in front of mccmain, within a few inches, but gets no injuries. just a nice sized flash of light and an audible pop.
- a few strands of copper melt off, but the entire ground wire is not severed.
- we tested and verified zero energy before and after the incident. tested oldmain, did meggers, checked for rodents, looked for backfeeding possibilities, e.t.c. but found nothing plausible.
my questions are: have any of you seen anything like that? what could be the cause? if it could have been residual voltage, can you have residual voltage significant enough to burn through a few strands of copper?