Do you/clients/consultants use the 125 kVA exception from IEEE 1584?
Yes 70%  70%  [ 48 ]
We use a variation (please explain) 6%  6%  [ 4 ]
No 23%  23%  [ 16 ]
Does not apply 1%  1%  [ 1 ]
Total votes : 69
Author Message
 Post subject: IEEE 1584 125 kVA transformer “Exception”
PostPosted: Sun Feb 18, 2018 9:58 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1727
Location: Scottsdale, Arizona
IEEE 1584 125 kVA transformer “Exception”

The conversation about the 125 kVA transformer “exception” comes up regularly and has surfaced not only at the Arc Flash Forum but in other recent conversations and e-mails that I have had. This is also a major topic of discussion during the revision process for the next edition of IEEE 1584.

The exact language from IEEE 1584-2002 is:

4.2 Step 1
“Equipment below 240 V need not be considered unless it involves at least one 125 kVA or larger low impedance transformer in its immediate power supply.”


It has been almost 16 years since this standard was published (September 2002) and years since I have asked this question. Thoughts and practices have evolved along the way so here is this week’s question.

Do you/clients/consultants use the 125 kVA exception from IEEE 1584?
-Yes
-We use a variation (please explain)
-No
-Does not apply


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584 125 kVA transformer “Exception”
PostPosted: Mon Feb 19, 2018 9:32 am 
Sparks Level

Joined: Fri Apr 15, 2011 7:43 am
Posts: 178
Location: Colorado
We have in the past ignored these "low powered" panels, as I call them. The problem is the qualified persons still need some sort of PPE to open the equipment up and a generic "Arc Flash Hazard Present" does little for our electrician friends. Recently I have been adopting the NESC approach from Table 410-1, especially knowing that the new 1584 is addressing the issue but not completely. With the NESC approach I can not put a label/PPE on the "low powered" equipment.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883