Welcome to the airfield lighting business! A word of caution to people new to airfield lighting. An airfield lighting series circuit complies with all the laws of physics. However, a current loop behaves very differently from our typical voltage distribution systems.
.
An airfield lighting series circuit is a current loop; thus, on the output of a constant current regulator (CCR), a short circuit is good, and an open circuit is bad. On a fully loaded 6.6-amp 30 kW CCR normal operating voltage will be approximately 4,545 volts, with the open circuit voltage approaching more than 9,000 volts. A CCR is designed to maintain a fixed current through the load by varying the output voltage. It is an ungrounded system; therefore, a single ground will have no impact on system operation. Two or more grounds will provide a parallel path for current and will likely impact the lumen output of the light fixtures between the two grounds. The CCR is designed to maintain this desired current flow, the CCR does not care if the load is a group of lamps or a person. The shock hazard on the secondary of a CCR is very real. Since short circuiting the output of a CCR is an accepted method of verifying proper CCR operation, in my humble opinion there is no arc-flash hazard on the output of the CCR. The operating characteristics of a CCR can be found in FAA Advisory Circular 150/5345-10H, Specification for Constant Current Regulators and Regulator Monitors available at
www.faa.gov.
.
Arc-Flash hazards and shock hazards are real issues on the input side of a CCR. The incoming AC power to the CCR presents the same characteristics as with other electrical equipment. The branch circuit feeding the CCR is typically far enough downstream from the source that the incident energy is low although not negligible. Each installation should be individually evaluated. Since both output and input may be closely adjacent in the CCR arc-flash hazards and shock hazards are both present within the CCR.