Ashdgee wrote:
wbd wrote:
I would make sure that you were provided with the latest available utility fault current. I contact the utility directly for that information.
It appears you are a consultant but this is your first arc flash study?
We got the fault levels from the municipal supply authority.I am a consultant , junior/mid level.The senior engineer will look at it.Im just giving myself a go while he's still away (on a project site out of the country).
However, I have recommended the company to get the latest version of ETAP as this will make our work very easier
Hi,
The concept of the enclosure editor in ETAP is the benefit from your latest version (ETAP 19.5). For your MCC bus, you can create a Bus and line side (incoming breaker) enclosure with the flexibility of entering different box sizes (Height, Width, Depth) for each BUCKET.
In addition, you can choose multiple configurations for each enclosure such as (VCB and VCBB) as well. ETAP reports the worst case of selected two configurations for each bucket defined plus accounting for different box size entered.
In ETAP 19.5, a new concept called C-area plots is introduced which can account for probabilistic variations in the box size to create an incident energy area (in the Time Current Curves TCC) curve as a function of time and current. This was also mentioned in the forum thread by Marcelo Valdes
The above concept is explained in detail in the last PCIC conference. The authors of the paper are from IEEE 1584-2018 task and working group committee. The details are as follows.
"Application of Incident Energy Reference Boundary Area Plots in TCCs considering IEEE 1584-2018 Input Parameter Variability" Paper No. PCIC-2019-40
For further details, you can contact ETAP as well. Hope it helps
Thank you
Regards
Raghu