rshummel wrote:
We have come across this recently and wonder if there has been any further clarification on the matter in any code? Within SKM there is the option to run the study and ignor any over duty equipment and I assume it's there for a reason. Would appreciate any further clarification that further explains this.
This is an issue that is still raised and there does not seem to be an industry consensus (which is why the question was asked some time ago)
The main issue that no one wants to point to is liability. If someone knows equipment was inadequate, there is a concern that completing the arc flash study and ignoring the inadequacy could come back to legally haunt them if something goes wrong. I think I recall a legal case to that effect – “but didn’t you know this when you performed the study?”
So, it does need acknowledged but the issue is how? Some will place a label with just a warning and no arc flash info, some place an arc flash label with a warning about the inadequacy, most will as a minimum document it in the report. As a minimum, it will likely upset the owner. From lots of experience, if you point out inadequate equipment to the owner (which you must do), they get all excited since now they own the liability and have a new item for their budget that does not have anything to do with process/production improvements.
Two thing I would NOT do is:
1) Skip labeling and not place anything on the equipment. That raises the question to the worker – did someone just forget this one?
2) Ignore the inadequacy.
Interested in what others have experienced?
Good luck!