It is currently Tue Mar 25, 2025 1:50 am



Post new topic Reply to topic
Author Message
 Post subject: Service entrance
PostPosted: Tue Feb 09, 2021 7:01 pm 

Joined: Fri Jul 10, 2009 10:14 am
Posts: 32
Location: West Central, OH
We keeping debating what defines a service entrance per NEC. Take a typical large facility with multiple buildings . We purchase power and then it goes through our transformers, distributed across the facility and more transformers to lower the voltage again. Is the service enterance where we take ownership or the secondary of every transformer?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Service entrance
PostPosted: Wed Feb 10, 2021 3:16 pm 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 133
willcoc wrote:
We keeping debating what defines a service entrance per NEC. Take a typical large facility with multiple buildings . We purchase power and then it goes through our transformers, distributed across the facility and more transformers to lower the voltage again. Is the service entrance where we take ownership or the secondary of every transformer?


IMHO, your service entrance is the feeders from your utility voltage transformation (e.g. 13.2kV to 480/277V or similar) to the main switchgear, switchboard, panelboard, etc. of each building.

If you are primary metered and have multiple large transformers for a campus system, then the demarcation point is called the "point of common coupling". This could be a metering cabinet owned by the utility, which then is the origination point of your campus electrical distribution system.

Mike

PS I'm sure there will be a few opinions on this.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Service entrance
PostPosted: Mon Feb 22, 2021 6:47 am 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 520
Location: New England
I agree. The service begins where the utility feeders end. Stop and think, the utility is not obligated to follow NEC. But your distribution on your campus is.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Service entrance
PostPosted: Mon Feb 22, 2021 11:59 am 
Sparks Level

Joined: Sat Apr 04, 2009 9:50 pm
Posts: 122
Location: San Antonio, TX
So the first disconnecting means AFTER the POINT OF SERVICE is your SERVICE DISCONNECT. Main disconnects after the transformers fed by this SERVICE DISCONNECT are not SERVICE DISCONNECTS. Are you interested in identifying the SERVICE DISCONNECTS for grounding purpuses?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Service entrance
PostPosted: Mon Mar 01, 2021 8:05 am 

Joined: Mon Oct 19, 2009 7:42 am
Posts: 32
Services can be low voltage or high voltage (NEC definition) depending how you obtain your supply from the local utility. At our plant, we receive 115kV service and then transform and distribute within our customer owned distribution system. The NEC handbook has some good explanation of this distinction for campus styled multibuilding complexes in Art 90.2, 225.32, and 695.3 (C). The definition of service has changed over the years and many older engineers and electricians still use the old definitions. I have attached a few docs I developed to help explain services to my workforce. They may be of use to you also.


Attachments:
Svc Xfmrs vs SDS.pdf [127.02 KiB]
Downloaded 42 times
Services vs. Bldgs Supplied by Feeder with text (NEC 2020).pdf [466.19 KiB]
Downloaded 45 times
Service Definitions.pdf [121.87 KiB]
Downloaded 43 times
Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883