It is currently Sun Sep 27, 2026 12:11 pm
What is the highest arc rating of PPE that you/clients use?
4 to 12 cal/cm2 6%  6%  [ 2 ]
Above 12 through 40 cal/cm2 65%  65%  [ 22 ]
Above 40 through 75 cal/cm2 15%  15%  [ 5 ]
Above 75 through 100 cal/cm2 9%  9%  [ 3 ]
Greater than 100 cal/cm2 6%  6%  [ 2 ]
N/A 0%  0%  [ 0 ]
Total votes : 34
 Post subject: PPE - Highest Arc Rating?
PostPosted: Sat Apr 10, 2021 4:59 am
What is the highest arc rating of PPE that you/clients use? (select range of arc rating)
4 to 12 cal/cm2
N/A
 Post subject: Re: PPE - Highest Arc Rating?
PostPosted: Mon Apr 12, 2021 7:08 am
We have done arc flash calculations for all of our quarries and have been successful at mitigating most Electrical panels to be under 8 Cal/cm and provide our electrical techs with 8 Cal/cm clothing. We have a very few situations with a higher than 8 Cal/cm, but have no need to enter those enclosures with power on and have done a great job with labeling as well as training to kill power before working in those areas.
PostPosted: Mon Apr 12, 2021 11:43 am
Great to hear! Controlling the risk by reducing the incident energy and establishing an electrically safe work condition are the way to go! Electrical safety has evolved so much over the years. I still recall the days of "The incident energy is... dress for it"