| Author |
Message |
diakonos1984
Post subject: How do you determine "compartmentalization"? Posted: Wed May 14, 2025 8:49 pm |
2018 IEEE 1584 6.10 says "When a model of the power system is developed, the equipment compartmentalization and fault location need to be considered. The arc fault could occur on the line side, bus side, and load side of protective devices located in different compartments... ...When evaluating the incident energy at an arcing fault location in the system, the interrupting time of the protective device upstream from the point of the fault must be considered. An integral “main” overcurrent protective device may be considered in the calculation if it is adequately isolated from the bus to prevent escalation to a line-side fault. When the integral main overcurrent protective device is not adequately isolated from the bus, the upstream protective device must be considered as protecting the main and bus."
I see lots of discussion on this subject and "propagation" on this forum in the early 2010s, but not much since the 2018 standard came out.
How are all of you currently determining/defining: "compartmentalization" and "adequately isolated"?
| Top |
mpparent
Post subject: Re: How do you determine "compartmentalization"? Posted: Thu May 15, 2025 5:15 am |
Engineering judgment based on the construction of the equipment.
Mike
| Top |
diakonos1984
Post subject: Re: How do you determine "compartmentalization"? Posted: Thu May 15, 2025 6:49 am |
Thanks, Mike. Are there standards or manufacturer's information that you are consulting? Do you have default assumptions? Or are you eyeballing it on a case-by-case basis?
| Top |
mpparent
Post subject: Re: How do you determine "compartmentalization"? Posted: Thu May 15, 2025 6:59 am |
I put eyes on it. Shop drawings for the equipment are helpful as well.
Mike
| Top |
JBD
Post subject: Re: How do you determine "compartmentalization"? Posted: Sat May 17, 2025 10:22 am |
Joined: Mon Jan 18, 2010 11:35 am Posts: 614 Location: Wisconsin
mpparent wrote: Engineering judgment based on the construction of the equipment. Basically gear built to UL standards, like switchboards and MCCs are not compartmentalized in a manner that would be beneficial for arc flash studies However, most medium voltage equipment such as switchgear and MCCs is compartmentalized. The iffy products are LV drawout switchgear where some is fully compartmentalized but some manufacturers have openings between the cross bussing and the cable compartments.
| Top |
diakonos1984
Post subject: Re: How do you determine "compartmentalization"? Posted: Mon Jun 09, 2025 5:08 am |
I have a hard time with Quote: MCCs are not compartmentalized Isn't that what buckets do? Each feeder bucket is isolated from the bus, and the main breaker is almost always in a different section. I have a hard time imagining a fault in a feeder bucket propagating to the line side of the main.
| Top |
diakonos1984
Post subject: Re: How do you determine "compartmentalization"? Posted: Mon Jun 09, 2025 5:09 am |
JBD, are there particular standards you refer to? E.g., UL gear = NOT compartmentalized, ANSI something gear = compartmentalized? Do those standards actually say anything on the subject, or is this your engineering judgment?
| Top |
mpparent
Post subject: Re: How do you determine "compartmentalization"? Posted: Wed Jun 11, 2025 6:06 am |
diakonos1984 wrote: JBD, are there particular standards you refer to? E.g., UL gear = NOT compartmentalized, ANSI something gear = compartmentalized? Do those standards actually say anything on the subject, or is this your engineering judgment? The standards JBD is referring do not talk about arc flash. Those references are equipment/construction standards. Mike
| Top |
JBD
Post subject: Re: How do you determine "compartmentalization"? Posted: Sat Aug 23, 2025 3:30 pm |
diakonos1984 wrote: I have a hard time with Quote: MCCs are not compartmentalized Isn't that what buckets do? Each feeder bucket is isolated from the bus, and the main breaker is almost always in a different section. I have a hard time imagining a fault in a feeder bucket propagating to the line side of the main. Most motor control center buckets are not sealed or even gasketed/ there is plenty of space around a bucket to allow an arc in a bucket to propagate to the sections vertical bus and then to the MCC cross bus. There is more than one horror story of screws, tools, and fuses rolling through the spaces in buckets.
| Top |
Page 1 of 1
[ 9 posts ] |
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot post attachments in this forum