| Author |
Message |
Joe Tedesco
Post subject: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Sat Feb 23, 2019 4:23 am |
Joined: Thu Feb 21, 2019 8:59 am Posts: 46 Location: Boston, Massachusetts 02113
I discovered this on my first day on the job, back in 1971 when I started as Chief Electrical Inspector for the City of Glendale, California.The service was energized, and the meters were set and sealed!  For this one I had to stop (was riding a Harley) and take a closer look? I scratched my head, got back on the bike and continued to the rest of my inspections for that day. We'll discuss them as we travel through my time line as an electrical inspector in Pasadena, CA, and previously as one in New Haven, Connecticut back in the 60's. I promise we'll have some fun! I gotta lot of stories to share with you all.
| Attachments: |
_________________ Joe Tedesco, NEC Consultant
| Top |
L. Hankle
Post subject: Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Sat Feb 23, 2019 9:50 am |
Since I doubt if the installer was a licensed electrician, were they at least a licensed plumber?
| Top |
Joe Tedesco
Post subject: Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Sat Feb 23, 2019 1:40 pm |
L. Hankle wrote: Since I doubt if the installer was a licensed electrician, were they at least a licensed plumber?  When I completed my inspections, I returned to my office and looked for the electrical permit and found that the installation was approved by a building inspector. I've traveled to Glendale in the past a found that property gone, and a new multistorey building in its place.
| Top |
Jim Phillips (brainfiller)
Post subject: Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Sun Feb 24, 2019 3:11 pm |
| Plasma Level |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1737 Location: Scottsdale, Arizona
Joe Tedesco wrote: [b]We'll discuss them as we travel through my time line as an electrical inspector in Pasadena, CA, and previously as one in New Haven, Connecticut back in the 60's. I promise we'll have some fun! I gotta lot of stories to share with you all.  Looking forward to the stories from your long career serving the electrical industry. Glad you can share with us!
| Top |
wilhendrix
Post subject: Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Mon Feb 25, 2019 8:56 am |
| Top |
bbaumer
Post subject: Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Mon Feb 25, 2019 11:22 am |
| Arc Level |
Joined: Fri Jul 08, 2016 10:01 am Posts: 489 Location: Indiana
wilhendrix wrote: Back in the 1970's when I was a service electrician, I worked at an aluminum extrusion factory. This was on a reservation just south of Phoenix. This installation still stands out as one for the record book. All of the pipe was plumbing pipe including the elbows. The panel was a NEMA 1 installed outside. The panel was running at 480 volts, but was a 120/208 volt panel with typical residential level breakers. Removing the dead front revealed all white wire along with several 10 and 12 gauge wires placed directly under the main lugs. The feeders were aluminum while the #10 and 12 wire (under the same main lugs) were copper. Finally, the panel was mounted on the side of a large heat treating unit. In the summer, I'd expect that the temperatures could easily reach 180F or higher. Seeing something like this, even on the "res" was surprising. Hey, man Attachment:
_________________ SKM jockey for hire PE in 17 states
| Top |
stevenal
Post subject: Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Tue Feb 26, 2019 9:16 am |
| Top |
bbaumer
Post subject: Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Tue Feb 26, 2019 10:29 am |
| Arc Level |
stevenal wrote: Jim needs to add a "like" button.
| Top |
ianmontgomery
Post subject: Re: PLUMBING ELBOWS INSTALLED IN SERVICE RACEWAY Posted: Thu May 07, 2026 3:08 am |
That’s the kind of inspection story you never forget. Back in the early 70s there were definitely some “creative” installations that somehow made it all the way through to an energized service. Using plumbing elbows in a service raceway sounds funny now, but it also shows why experienced inspectors mattered so much in catching unsafe shortcuts before they turned into bigger problems. I’ve seen similar discussions from tradespeople over at Plumber Singapore, where plumbers mention running into electrical setups that clearly crossed trade boundaries in the wrong way. It usually comes down to someone trying to make materials “work” instead of using code-approved components. Different era, but the same lesson still applies today. Looking forward to hearing more of those inspection stories from Pasadena and New Haven. The old field experiences are often better learning material than textbooks.