It is currently Tue Oct 13, 2026 2:50 am
 Post subject: Arcing Time for 132kV
PostPosted: Thu Sep 17, 2009 12:17 am
i intrested to do hand calculation for arc flash hazard for 33kV and 132kV. I face some problem in finding arcing time. May i know is arcing time equal to fault clearing time? How to get the arcing time for 33kV and 132kV switchgear and cables? Is it any standard that i can refer to? Thanks in advance.
Yuna :o
PostPosted: Thu Sep 17, 2009 4:01 am
The fault/arc clearing time will be determined by the protective device types and settings. These must be found from calibration/testing reports or by actual field tests for each device. There is no standard for that.