It is currently Sun Oct 11, 2026 12:38 am
 Post subject: Stop Arc flash on a transformer
PostPosted: Thu Jul 02, 2009 8:32 am
Does anyone have any ideas on how to stop arc flashes on a transformer without short circuiting it? We've thought of enclosing it in a grounded housing where the air vents are located on the bottom allowing the flash to blow out the top. Currently the air vents are located on the side allowing a possible arc to permiate through the spaces.
PostPosted: Thu Jul 02, 2009 9:12 am
Am I missing something? Won't tripping the primary protective device stop the arc?
PostPosted: Mon Jul 06, 2009 5:48 am
Depending on your system configuration you could implement a transformer differential scheme. This would clear a fault on the primary or secondary windings much quicker than typical overcurrent devices.
PostPosted: Thu Jul 16, 2009 1:06 pm
What I'm looking at is ABB's REA 101
PostPosted: Thu Jul 16, 2009 1:14 pm
WHat type of transformer (ratings)are you talking about? What is the OCPD on the primary?
PostPosted: Mon Sep 14, 2009 12:27 pm
I just looked up this ABB part. No answer to your question. But I have to read about this part more. It seems interesting. I wonder how much it cost.
PostPosted: Wed Nov 18, 2009 10:46 pm
that's an issue with some dry type transformer
they are vented between elbow and eye level that is kind of dangerous
some other model are at bottom and top of tranformer door those are more secure in case of a flash if you are near by
