THE CABLE GUY wrote:
Sorry, WDN
I am so dumb I just do not understand the question.
Considering the number of times you've agreed with me lately, I must respectfully disagree with this assessment.
THE CABLE GUY wrote:
hmm, I was under the impression an ungrounded system had less arcing fault current.
Were do you see in 1584 that K2 for ungrounded is greater then 0?
...
I have little experance with ungrounded systems and hope to never have to figure one out. I know several places use HRG but I don't know much about that other then what I have read.
CG -
We are currently moving to resistance grounded systems on most of our 480V systems. The other engineers don't understand when I tell them this is actually making our arc flash hazard worse! As you say, the impression (and probably the fact) is that ungrounded or HRG systems are safer.
The problem in the 1584 calculations come on page 11 of the IEEE 1584a-2004. Equation 4 is the equation to find Incident Energy from Arcing Current. The K2 factor is 0 for ungrounded, but -0.133 for grounded systems. This negative results in lower energy levels for grounded systems.
I'm at a loss as to the WHY an ungrounded or HRG system would have higher energy levels. I may have had it explained to me at one time, but slept since that discussion.