It is currently Sat Oct 24, 2026 11:00 pm
 Post subject: Coordination & Short Circuit Study
PostPosted: Thu Sep 09, 2010 8:57 am
Hi,
Sorry if this is not the right forum to bring up this question or if it has been dealt with before.
If a spec calls for just coordination study - do I also need to perform short circuit study and include the results of this analysis in the report.
Now I know that short circuit calculations need to be performed as part of the coordination study to determine to what extent protective devices selectively coordinate. But I am just not sure if the results (probably a table indicating if switchboards'/panels' SC rating pass/fail in comparison to the calculated fault levels at these locations) shall be included along with the findings of the coordination study
Thanks for the help
PostPosted: Fri Sep 10, 2010 10:51 am
There is no standard as to what to include in a coordination study report. Normally, you would include the results of the short circuit study. What results and to what detail is a matter of judgement and agreement with whoever you are doing the report for.