321Liftoff wrote:
We are having a debate about what PPE is required when working in manholes. Are the Medium Voltage (13.8kV) cable splicers allowed to work in a manhole with category 1 (preferred) or 2 PPE to perform the splice even though there are other live MV cables in the area?
The manhole is inspected first wearing Cat 2 PPE and the Feeder Breaker relay settings are set low (hair trigger) for all cables within the manhole, prior to entrance for any activity.
The obvious problem we are having is not wanting to wear excessive PPE down in the manhole.
How have people been handling this?
Great question, I have agood solution, the last company I worked for did dozens of MV splices a day, so I had to research and devise a solution, granted it is not perfect, but it combines safety with workability.
1. Do all the manhole entering stuff that has nothing to do with arc flash (Confined space rigamaroll)
2. Don 40 Cal suit
3. Enter manhole, wrap other cables with arc flash suppression blankets
4. Exit manhole, get some air, don HRC 2 PPE
5. Re-enter, work in HRC 2