It is currently Sat Oct 24, 2026 11:14 am
 Post subject: Arc-Flash PPE question
PostPosted: Thu May 12, 2011 9:43 am
What PPE category should I use as a guideline if my Incident Engergy is 7.5 cal/cm2? HRC 2 or HRC 2*? The main difference between the two is that for HRC 2* you need a Balaclava Hood. How do I determine if I need a Balaclava Hood?
PostPosted: Thu May 12, 2011 10:34 am
Hrc 2*
In the 2012 edition of the NFPA-70E there will no longer be a distinction between HRC 2 and HRC 2* so either a face shield + balaclava or a flash suit hood will be required.
[url="http://www.necplus.org/Features/Pages/FullHeadProtectionBiddingadieutothe2hazardriskdesignation.aspx?sso=0"]Full Head Protection: Bidding adieu to the 2* hazard/risk designation[/url]
by Jeffrey S. Sargent
PostPosted: Thu May 12, 2011 10:43 am
Hrc 2*
Thank you very much.
PostPosted: Wed Jun 08, 2011 10:59 am
Thank goodness they finally made a decision on this subject. Any idea when we will see the 2012 addition?