Post subject: Incident Energy Calc of Faulted MV Cable in Manhole Posted: Wed Jun 29, 2011 1:25 pm |
|
Joined: Mon Oct 19, 2009 7:42 am Posts: 32
|
|
It has been suggested by some of my colleagues that IEEE 1584 equations can be used to calculate the incident energy resulting from a faulted MV cable in a manhole. Am I correct in my understanding that the equations in IEEE 1584 are only applicable to a fault between conductors having an air gap? If this is correct, I don't see how the equations are applicable to finding the incident energy of a faulted medium voltage cable that won't have any air gap between phases or to the grounded shield. The only way I can trick the software to making this calculation is to insert a bus with an air gap at the manhole location, but this does not realistically model a faulted cable or splice and I don't have any confidence in the results. Does anyone have any experience or guidance with this situation?
|
|
| Top |
|
 |
|
Zog
|
Post subject: Posted: Wed Jun 29, 2011 5:22 pm |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
|
I agree with you, not to mention you are in a manhole and the dynamics of the whole space are different.
|
|
| Top |
|
 |
|