PostPosted: Thu Oct 07, 2010 12:38 pm 
Sparks Level

Joined: Wed Jun 02, 2010 12:59 pm
Posts: 70
Location: Milwaukee WI
I first read about the ABB TVOC-2 on this site. Subsequently, I downloaded and read the ABB literature. Looks good, any first hand experience users here with TVOC-2 or TVOC, the predecessor?

One TVOC-2 characteristic struck me, current sensing is an option. It might be valid to exclude current sensing, particularly if the optical sensors are well protected from spurious light.

More on this later perhaps, still considering recent experience with another optical/current relay install. Testing the optical portion is simple, but doing a current and optical test is more challenging, because equipment must be powered and running to have real world amps in the test.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Oct 20, 2010 4:01 am 

Joined: Wed Jun 03, 2009 3:43 am
Posts: 10
Current injection + camera flash

You can use some kind of currect injection device and a camera flash to test light & current based arc-flash protection. Not too difficult.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Oct 22, 2010 11:32 am 
Sparks Level

Joined: Wed Jun 02, 2010 12:59 pm
Posts: 70
Location: Milwaukee WI
Testing optical sensing relays.

Need a current injection device to emulate 3 CT signals, each 120 degrees phase shifted. Need ability to vary and record applied current. Each phase individually, or in groups of 2 or 3. Does any vendor offer such a portable test instrument? My good old Fluke Processmeter could source 4-20 mA, DC, but that was it.

Then using camera strobe is no real problem, as long as cabinet covers can be removed.

Also have to remember to short secondaries of any CTs disconnected for relay test purposes.

Final test needs to be full power, but then cabinets need to be closed. Need a remotely triggered strobe. Some will trigger by light as a slave from another strobe, but how to get that light through an enclosure wall?

These and more are issues I am pondering...


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Nov 02, 2010 1:18 am 

Joined: Wed Jun 03, 2009 3:43 am
Posts: 10
Current injection device

Need a current injection device?

- Freja 3000
- Omicron CMC 356 or 256


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Dec 23, 2010 3:00 am 

Joined: Thu Dec 23, 2010 2:44 am
Posts: 1
Link to intruction manual

Hi both,

Since I'm working with these products and found your question alittle bit late on this forom. Here you can find the instruction manual. I think the testing is on page 6 for CSU.

As you said it's not to be considered a standard solution, and you are right it's more tricky to test the over current in an as reliable way. But in some cases necessary. As seen in this manual you can simulate overcurrent by turning the potentiometers in the products in the correct way (see manual).

[url="http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/605f33a4de4a246dc1256dd0003765ea/$File/1SFA663007R1001%20Ed%201,%20October%202003%20(English).pdf"]Link to manual[/url]

Best Regards,

Richard Petersson Wigh


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883