Hi can some one guide me on the following things.
  1. What are the major changes in NFPA 2012 compared to previos version.
  2. How Can we implement NFPA 70e 2012 using PTW 6.5 version.
  3. If yes kindly guide the procedure. Thanks in advance for help.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Dec 10, 2013 11:45 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 881
Location: Rutland, VT
1. If you purchase NFPA 70E-2012, you will find a synopsis of the changes in the Foreword as well as the changes highlighted throughout the document.

2. Can't help there as I use EasyPower but they have updated to follow the need NFPA 70E. I would imagine that if you have a yearly maintenance contract, PTW does the same. Any PTW users will comment I am sure.

3. See #1 above.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Dec 17, 2013 10:04 am 
Sparks Level

Joined: Mon Jun 07, 2010 9:40 am
Posts: 119
I don't remember when 6.5 came out, but I think it was before the update.

That doesn't mean you can't comply, but the most simple method is pay your maintenance fee and update to version 7 of PTW


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Jan 12, 2014 7:24 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
70E does not directly support any particular analysis method. Thus PTW is unaffected. The only "change" is that the 125 kva rule was dropped. It has not been changed in IEEE 1584 yet, and this is all outside 1584.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883