 Post subject: About ONAN and ONAF transformer.
PostPosted: Mon Jan 20, 2014 11:21 pm 

Joined: Thu Jan 16, 2014 10:02 pm
Posts: 16
Location: pune
While doing the transformer modeling with ONAN and ONAF ratings pl let me know if we put in skm transformer page in nominal rating ONAN rating and full load rating as ONAF rating whether the software will consider the ONAF rating during any course of time.If so at what stage?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Jan 27, 2014 9:28 am 

Joined: Wed Feb 01, 2012 10:44 am
Posts: 22
Location: Atlanta, GA
For SKM input data, use ONAN = Nominal KVA and ONAF = Full Load KVA. Fault calculations (and therefore arc flash, also transient stability, motor starting, etc.) will use the ONAN rating for impedances, and ONAF will have no impact. Load flow studies would use the ONAF rating to evaluate overloading the transformer.