It is currently Thu Nov 05, 2026 10:57 pm
 Post subject: Derating Factor (X/R ratio)
PostPosted: Wed Mar 04, 2009 12:15 pm
What if the symmetrical fault current is the same as the equipment’s rated current,
but the actual X/R ratio is larger than the tested X/R ratio? (MF=Iasym @ X/Rtestd-:-Iasy @X/Rcalc)
PostPosted: Wed Mar 04, 2009 12:58 pm
Not unless you have the sequence info as well. Unless it is very high then not a big deal anyway since most equipment is designed for x/r>1 per the standards.
If I remember correctly, Vacuum Circuit Breakers are required by the ANSI/IEEE standards to interrupt at rated AIC with an offset associated with an x/r=15.