Post subject: Derating Factor (X/R ratio) Posted: Wed Mar 04, 2009 12:15 pm |
|
Joined: Fri Jun 06, 2008 12:59 pm Posts: 3 Location: Winnipeg, MB Canada
|
|
What if the symmetrical fault current is the same as the equipment’s rated current,
but the actual X/R ratio is larger than the tested X/R ratio? (MF=Iasym @ X/Rtestd-:-Iasy @X/Rcalc)
|
|
| Top |
|
 |
|
acobb
|
Post subject: Posted: Wed Mar 04, 2009 12:58 pm |
|
Joined: Sun Dec 23, 2007 1:44 pm Posts: 348 Location: Charlotte, NC
|
|
Not unless you have the sequence info as well. Unless it is very high then not a big deal anyway since most equipment is designed for x/r>1 per the standards. If I remember correctly, Vacuum Circuit Breakers are required by the ANSI/IEEE standards to interrupt at rated AIC with an offset associated with an x/r=15.
|
|