I am starting to do self-study the IEEE 1584:2018 standard for arc-flash calculation.
During the reading of the data from Table 2 Coefficient for Equation (2), I found there is different written of wording.

For. e.g, for K2 factor:
"−6.0287E-05" for VCBB is described and "−3.097e-06" for HCB is used.

My question is for "e" in the table data sheet is it just mistake which shall be to "E" instead? for e.g, "−3.097e-06" corrected to "−3.097E-06" = "-3.097x10-6".or,
there is different meaning for "e", for e.g, "natural logarithm"?
Thanks for your help.


Attachments:
Table 2 of IEEE 1584 Y2018.JPG
Table 2 of IEEE 1584 Y2018.JPG [ 55.73 KiB | Viewed 3995 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: regarding to "e" and "E" used in Table 2 of Coefficient
PostPosted: Sun Aug 27, 2023 5:07 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
I believe that is a typo since these are all coefficients in scientific notation.
It has been added to the list for next time.

Thanks!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883