| Author |
Message |
Billy XU
Post subject: regarding to "e" and "E" used in Table 2 of Coefficient Posted: Sun Aug 27, 2023 3:06 am |
Hello everyone. I am starting to do self-study the IEEE 1584:2018 standard for arc-flash calculation. During the reading of the data from Table 2 Coefficient for Equation (2), I found there is different written of wording.
For. e.g, for K2 factor: "−6.0287E-05" for VCBB is described and "−3.097e-06" for HCB is used.
My question is for "e" in the table data sheet is it just mistake which shall be to "E" instead? for e.g, "−3.097e-06" corrected to "−3.097E-06" = "-3.097x10-6".or, there is different meaning for "e", for e.g, "natural logarithm"? Thanks for your help.
| Attachments: |
| Top |
Jim Phillips (brainfiller)
Post subject: Re: regarding to "e" and "E" used in Table 2 of Coefficient Posted: Sun Aug 27, 2023 5:07 pm |
| Plasma Level |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1738 Location: Scottsdale, Arizona
I believe that is a typo since these are all coefficients in scientific notation. It has been added to the list for next time.
Thanks!
| Top |
Page 1 of 1
[ 2 posts ] |
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot post attachments in this forum