It is currently Wed Oct 28, 2026 1:11 am



Post new topic Reply to topic
Author Message
 Post subject: Series Rating
PostPosted: Fri Mar 14, 2025 12:55 pm 

Joined: Fri Mar 14, 2025 12:52 pm
Posts: 2
Would the lowest rated breaker be able to be series rated on a MLO panel? See picture


https://pasteboard.co/opibe0XafPjG.png


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Rating
PostPosted: Fri Mar 14, 2025 1:57 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Series ratings between circuit breakers is determined by tests such as U.L. Therefore you have to consult the circuit breaker manufacture to see what combinations will work. Also, the NEC prohibits series ratings if there is any short circuit current such as motor contribution, being introduced between the two devices that exceeds 1% of the interrupting rating.

Check with the circuit breaker manufacturer's website. They should have the combinations listed.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Rating
PostPosted: Fri Mar 14, 2025 2:04 pm 

Joined: Fri Mar 14, 2025 12:52 pm
Posts: 2
@jim

Thanks Jim, I shouldve clarified. I have checked and they are series rated, but my question was more so for the configuration of the consectuive MLO panels


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Series Rating
PostPosted: Sat Mar 15, 2025 5:45 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Yes, for all three of your MLO panels and the feeder breaker as there are no other fuses or breakers in between. At least that is my understanding.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883