It is currently Tue Oct 27, 2026 9:28 pm
 Post subject: Series Rating
PostPosted: Fri Mar 14, 2025 12:55 pm
Would the lowest rated breaker be able to be series rated on a MLO panel? See picture
https://pasteboard.co/opibe0XafPjG.png
 Post subject: Re: Series Rating
PostPosted: Fri Mar 14, 2025 1:57 pm
Series ratings between circuit breakers is determined by tests such as U.L. Therefore you have to consult the circuit breaker manufacture to see what combinations will work. Also, the NEC prohibits series ratings if there is any short circuit current such as motor contribution, being introduced between the two devices that exceeds 1% of the interrupting rating.
Check with the circuit breaker manufacturer's website. They should have the combinations listed.
PostPosted: Fri Mar 14, 2025 2:04 pm
@jim
Thanks Jim, I shouldve clarified. I have checked and they are series rated, but my question was more so for the configuration of the consectuive MLO panels
PostPosted: Sat Mar 15, 2025 5:45 am
Yes, for all three of your MLO panels and the feeder breaker as there are no other fuses or breakers in between. At least that is my understanding.