It is currently Thu Oct 08, 2026 11:21 pm



Post new topic Reply to topic

What are your/company preferences for arc flash labels?
Nominal Voltage 17%  17%  [ 36 ]
Arc Flash Boundary 15%  15%  [ 32 ]
Incident Energy and Working distance 17%  17%  [ 36 ]
Arc Flash PPE Category 5%  5%  [ 10 ]
Minimum arc rating of clothing 8%  8%  [ 16 ]
Site specific PPE level 6%  6%  [ 12 ]
Limited and Restricted approach boundary 11%  11%  [ 24 ]
Date 15%  15%  [ 31 ]
List of PPE requirements 6%  6%  [ 12 ]
Something else - please tell us! 1%  1%  [ 3 ]
Total votes : 212
Author Message
 Post subject: Arc Flash Label Data - Revisted
PostPosted: Sun Oct 24, 2021 12:57 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
Arc flash (equipment) labels and data have been discussed in the past but practices evolve over time.

The 2021 Edition of NFPA 70E has minimum requirements for labels which includes:

(1) Nominal System Voltage 130.1(H)(1)
(2) Arc Flash Boundary 130.1(H)(2)
(3) At least one of the following:
a. Available incident energy and the corresponding working distance OR the arc flash PPE category
b. Minimum arc rating of clothing
c. Site-specific level of PPE

Here are a couple of references regarding labeling:

Article: Arc Flash Labels Simplified

Arc Flash Labeling Requirements and Strategies Free On Demand Video Class

To gauge the evolution of labeling, this week’s question is a follow up to a similar question asked quite some time ago.

What are your/company preferences for arc flash labels?

• Nominal Voltage
• Arc Flash Boundary
• Incident Energy and Working distance
• Arc Flash PPE Category
• Minimum arc rating of clothing
• Site specific PPE level
• Limited and Restricted approach boundary
• Date
• List of PPE requirements
• Something else - please tell us!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Label Data - Revisted
PostPosted: Mon Oct 25, 2021 10:33 am 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 201
Location: Maple Valley, WA.
We also include the following items:

1. Our company name.
2. Our company phone number.
3. Our Job #. (this is helpful for when we do a AF refresh study after 5 years.)
4. Maximum available fault current.
5. Standard Version used to calculate the AF energy and boundaries.


Attachments:
Arc Flash Label.JPG
Arc Flash Label.JPG [ 65.77 KiB | Viewed 94162 times ]

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Label Data - Revisted
PostPosted: Mon Oct 25, 2021 1:04 pm 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
I would add that Robert's example above also contains an ANSI signal word and symbol.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Label Data - Revisted
PostPosted: Tue Oct 26, 2021 7:54 am 

Joined: Fri Sep 24, 2021 7:17 am
Posts: 39
Having the maximum available fault current is a huge plus. I think by adding that number people will gain a much better appreciation of what arc flash energy is all about. Strangely, too many people order gear without even knowing what the available fault current even is.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883