Hello!
I am working on my own spreadsheet for the calculation of incident energy in accordance with IEEE 1584-2018.
I wonder if anyone can share numerical examples DIFFERENT from those provided by the standard in Annex D, for validation? I mean, with different types of enclosure, voltages, etc.
Thanks,
Sato


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Mon Apr 20, 2020 3:50 pm 

Joined: Sun Jul 22, 2007 5:00 pm
Posts: 36
Location: Stratham, SW Australia
Hello Sato
I have developed an IEEE 1584-2018 excel spreadsheet for simple one contribution radial feeder. ( as IEEE1584 Annnex D.1 and D.2 )
Send example input data:
Voc, Ibf, Gap, Working Distance, bus configuration, enclosure H X W X D, time-current curves for the one ( only ) protective devicve which clears the arcing current.
I will check the example using my spreadsheet and PTW32 Ver 9006.
Murray


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Tue Apr 28, 2020 6:35 am 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
efmsato wrote:
I am working on my own spreadsheet for the calculation of incident energy in accordance with IEEE 1584-2018.
I wonder if anyone can share numerical examples DIFFERENT from those provided by the standard in Annex D, for validation? I mean, with different types of enclosure, voltages, etc.


Please consider signing up free for AFA arc flash analysis web app online at https://app.arcadvisor.com and running any case scenarios you need to compare against your spreadsheet calcs. Once you've signed up, feel free to contact me and I'll unlock all the app features for you and anyone interested reading this post at ArcFlash forum for a couple of months.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Thu Apr 30, 2020 8:25 am 

Joined: Wed Mar 25, 2020 9:48 am
Posts: 3
Location: Porto Alegre - RS - BRAZIL
arcad wrote:
efmsato wrote:
I am working on my own spreadsheet for the calculation of incident energy in accordance with IEEE 1584-2018.
I wonder if anyone can share numerical examples DIFFERENT from those provided by the standard in Annex D, for validation? I mean, with different types of enclosure, voltages, etc.


Please consider signing up free for AFA arc flash analysis web app online at https://app.arcadvisor.com and running any case scenarios you need to compare against your spreadsheet calcs. Once you've signed up, feel free to contact me and I'll unlock all the app features for you and anyone interested reading this post at ArcFlash forum for a couple of months.


Dear Michael,
I appreciate your cooperation. I signed up for ArcAdvisor, I found it a great tool. I would like to do a test with medium voltage calculations. Would it be possible to have this functionality temporarily for evaluation?
Thank you!
Edson Sato


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Thu Apr 30, 2020 8:27 am 

Joined: Wed Mar 25, 2020 9:48 am
Posts: 3
Location: Porto Alegre - RS - BRAZIL
mnewman wrote:
Hello Sato
I have developed an IEEE 1584-2018 excel spreadsheet for simple one contribution radial feeder. ( as IEEE1584 Annnex D.1 and D.2 )
Send example input data:
Voc, Ibf, Gap, Working Distance, bus configuration, enclosure H X W X D, time-current curves for the one ( only ) protective devicve which clears the arcing current.
I will check the example using my spreadsheet and PTW32 Ver 9006.
Murray


Dear Murray,

I appreciate your message. I did not visit the Arc Flash Forum for a few days, so I just got your message. I hope everyone is doing well in your country. I am sure that we will soon overcome this difficult moment.

The spreadsheet I developed is "IEEE1584-2018_v5.xlsx". The spreadsheet is already filled in with data from Appendix D.1 and D.2 (lines 8-9), in addition to data from a case study I am working on (lines 10-22).

I would appreciate it if you can reproduce the results in your spreadsheet for comparison.

Regards,

Edson Sato


Attachments:
IEEE 1584-2018_v5.xlsx [56.1 KiB]
Downloaded 729 times
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Thu Apr 30, 2020 9:09 am 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
efmsato wrote:
arcad wrote:
efmsato wrote:
I am working on my own spreadsheet for the calculation of incident energy in accordance with IEEE 1584-2018.
I wonder if anyone can share numerical examples DIFFERENT from those provided by the standard in Annex D, for validation? I mean, with different types of enclosure, voltages, etc.


Please consider signing up free for AFA arc flash analysis web app online at https://app.arcadvisor.com and running any case scenarios you need to compare against your spreadsheet calcs. Once you've signed up, feel free to contact me and I'll unlock all the app features for you and anyone interested reading this post at ArcFlash forum for a couple of months.


Dear Michael,
I appreciate your cooperation. I signed up for ArcAdvisor, I found it a great tool. I would like to do a test with medium voltage calculations. Would it be possible to have this functionality temporarily for evaluation?
Thank you!
Edson Sato


Thanks for your favorable feedback, Edson. I've granted you two months full access to the resource.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Tue May 05, 2020 7:02 am 

Joined: Tue Aug 26, 2008 7:15 am
Posts: 6
Hello Michael.....I too have developed my own spreadsheet and wish to verify my calculations. I have also signed up to use your spreadsheet via the link you provided previously. I would appreciate the opportunity to utilize the functionality of your program as you have offered.

Thank you!

Ernie Bowles


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Tue May 05, 2020 7:08 am 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
ebowles wrote:
Hello Michael.....I too have developed my own spreadsheet and wish to verify my calculations. I have also signed up to use your spreadsheet via the link you provided previously. I would appreciate the opportunity to utilize the functionality of your program as you have offered.

Thank you!

Ernie Bowles

Hi Ernie,

As requested, I've granted you two months free access to the arc flash analysis web app.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Wed May 06, 2020 2:28 pm 

Joined: Tue Aug 26, 2008 7:15 am
Posts: 6
Thank you very much!

Ernie Bowles


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Sat Mar 06, 2021 9:12 pm 

Joined: Sun Jul 22, 2007 5:00 pm
Posts: 36
Location: Stratham, SW Australia
Hello Sato
Sorry for the delayed reply.
Your spreadsheet IEEE1584-2018_V5.xlsx is awesome !
Your results for the PN-01A, PN-01B, PN-02A, PN-04A and PN-07 scenarios agree with my IEEE1584-2018 spreadsheet results. (errors +/- 0.2% )
I will check your other scenarios later.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584-2018 calculation examples.
PostPosted: Sun Nov 28, 2021 1:59 am 

Joined: Sat Nov 27, 2021 12:43 am
Posts: 1
arcad wrote:
efmsato wrote:
I am working on my own spreadsheet for the calculation of incident energy in accordance with IEEE 1584-2018.
I wonder if anyone can share numerical examples DIFFERENT from those provided by the standard in Annex D, for validation? I mean, with different types of enclosure, voltages, etc.


Please consider signing up free for AFA arc flash analysis web app online at https://app.arcadvisor.com and running any case scenarios you need to compare against your spreadsheet calcs. Once you've signed up, feel free to contact me and I'll unlock all the app features for you and anyone interested reading this post at ArcFlash forum for a couple of months.


Hi Michael,

Could I please request that you unlock the web app for the arcflash calc so that I can test drive it?

Thanks
Joseph Ken


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 11 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883