 Post subject: Gloves
PostPosted: Fri Jan 16, 2009 2:25 pm 

Joined: Tue Jan 13, 2009 6:34 pm
Posts: 7
Location: Naugatuck, CT
Does anyone know if you can use line gloves with leather rated for ANSI/ASTM Class 00 D120 type 1 , 500V AC MAX in a level 2 AF area or do you need different gloves? Reason I ask is because I cant find any level 2 gloves on the web only 3 & 4 so do the want you to level up, or are the ones I have ok? Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Jan 16, 2009 7:04 pm 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
ctsmiths wrote:
Does anyone know if you can use line gloves with leather rated for ANSI/ASTM Class 00 D120 type 1 , 500V AC MAX in a level 2 AF area or do you need different gloves? Reason I ask is because I cant find any level 2 gloves on the web only 3 & 4 so do the want you to level up, or are the ones I have ok? Thanks


The rubber gloves with the leather protectors is sufficient hand protection.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Feb 28, 2009 7:45 pm 
Sparks Level

Joined: Sun Sep 23, 2007 5:00 pm
Posts: 152
Location: Calgary, Alberta, Canada
FYI, Hugh Hotgland was hired by one of the rubber insulating glove manufacturers and the rubber insulating gloves (black color) with the leather protector can provide significant arc flash protection in the 50-90 cal/cm2 range.

Regards;
Terry Becker, P.Eng.
http://www.esps.ca


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883