 Post subject: IEEE 1584 Equation Glitch
PostPosted: Fri Mar 04, 2011 5:55 am 
Offline
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1207
Location: Scottsdale, Arizona
There is an interesting glitch with the IEEE 1584 equation for arcing short circuit current at or above 1 kV.

The equation for arcing current at higher voltages > 1 kV:

Log Ia = 0.00402 + [0.983 (Log Ibf)]
Ia = 10^(Log Ia)

Where:
Ibf = 3 phase bolted short circuit current in kA
Ia = 3 phase arcing short circuit current
IEEE range of validity 700A to 106 kA

Here’s the glitch. If the bolted current is 1,000 Amps i.e. 1 kA:

Log Ia = 0.00402 + 0.983 X Log (1)

Log of 1 = 0
Therefore:

Log Ia = 0.00402 + 0.983 X 0
Log Ia = 0.00402 + 0
Log Ia = 0.00402

Ia = 10^(Log Ia)
Ia = 10^0.00402 = 1.0093 kA

So….. Ibolted = 1,000 Amps and Iarcing =1,009.3 Amps

Except it is physically impossible to have Iarcing greater than Ibolted.

Oops! :eek:

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 04, 2011 6:29 am 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
brainfiller wrote:
Except it is physically impossible to have Iarcing greater than Ibolted.

Oops! :eek:


Not very surprising since the IEEE 1584 equations were curve-fitted from the actual data. Some points will be over or under what's physically possible.

It somehow reminds me of 2 AA batteries of mine which, after use, had a negative voltage between the ends (-0.2 V and -0.3 V). I think they gave me too much energy, and now try to get some of it back. Not going to happen...


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 04, 2011 6:54 am 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 409
Location: Spartanburg, South Carolina
The glitch is only relevant for bolted faults < 1.734 kA. This probably won't affect many high incident energy locations.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 04, 2011 8:33 am 
Offline
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1207
Location: Scottsdale, Arizona
jghrist wrote:
The glitch is only relevant for bolted faults < 1.734 kA. This probably won't affect many high incident energy locations.


I am sure you are quite correct. I can't imagine that low of a current even sustaining easily.

Just thought the little(?) hiccup was interesting.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 17, 2011 1:35 pm 
Offline
Sparks Level
User avatar

Joined: Mon Jul 09, 2007 11:43 pm
Posts: 51
Location: Sheffield, England
Hi Jim, I came up with a similar scenario for voltages under and approaching 1000 volts about three years ago. I said at the time "how can you get an arcing current which is greater than the bolted current. You can easily get arcing current which is 50% higher than the bolted short circuit current value. WDeanT kindly posted the following link which is very interesting. The perils of curve fitting equations!!!


http://us.ferrazshawmut.com/arcflash/getting_help/downloads/ICPS-wilkins011904_web.pdf


Original thread
http://www.arcflashforum.com/showthread.php?t=74


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 18, 2011 3:04 am 
Offline
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1207
Location: Scottsdale, Arizona
Mike Frain wrote:
Hi Jim, I came up with a similar scenario for voltages under and approaching 1000 volts about three years ago. I said at the time "how can you get an arcing current which is greater than the bolted current. You can easily get arcing current which is 50% higher than the bolted short circuit current value. WDeanT kindly posted the following link which is very interesting. The perils of curve fitting equations!!!


http://us.ferrazshawmut.com/arcflash/getting_help/downloads/ICPS-wilkins011904_web.pdf


Original thread
http://www.arcflashforum.com/showthread.php?t=74


Hi Mike,

Forgot about that post. Good info!

Thanks!

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883