It is currently Fri Oct 02, 2026 11:04 pm
 Post subject: IEEE 1584 Equation Glitch
PostPosted: Fri Mar 04, 2011 5:55 am
There is an interesting glitch with the IEEE 1584 equation for arcing short circuit current at or above 1 kV.
The equation for arcing current at higher voltages > 1 kV:
Log Ia = 0.00402 + [0.983 (Log Ibf)]
Ia = 10^(Log Ia)
Where:
Ibf = 3 phase bolted short circuit current in kA
Ia = 3 phase arcing short circuit current
IEEE range of validity 700A to 106 kA
Here’s the glitch. If the bolted current is 1,000 Amps i.e. 1 kA:
Log Ia = 0.00402 + 0.983 X Log (1)
Log of 1 = 0
Therefore:
Log Ia = 0.00402 + 0.983 X 0
Log Ia = 0.00402
Ia = 10^(Log Ia)
Ia = 10^0.00402 = 1.0093 kA
So….. Ibolted = 1,000 Amps and Iarcing =1,009.3 Amps
Except it is physically impossible to have Iarcing greater than Ibolted.
Oops! :eek:
PostPosted: Fri Mar 04, 2011 6:29 am
Oops! :eek:
Not very surprising since the IEEE 1584 equations were curve-fitted from the actual data. Some points will be over or under what's physically possible.
It somehow reminds me of 2 AA batteries of mine which, after use, had a negative voltage between the ends (-0.2 V and -0.3 V). I think they gave me too much energy, and now try to get some of it back. Not going to happen...
PostPosted: Fri Mar 04, 2011 6:54 am
The glitch is only relevant for bolted faults < 1.734 kA. This probably won't affect many high incident energy locations.
PostPosted: Fri Mar 04, 2011 8:33 am
I am sure you are quite correct. I can't imagine that low of a current even sustaining easily.
Just thought the little(?) hiccup was interesting.
PostPosted: Thu Mar 17, 2011 1:35 pm
Hi Jim, I came up with a similar scenario for voltages under and approaching 1000 volts about three years ago. I said at the time "how can you get an arcing current which is greater than the bolted current. You can easily get arcing current which is 50% higher than the bolted short circuit current value. WDeanT kindly posted the following link which is very interesting. The perils of curve fitting equations!!!
http://us.ferrazshawmut.com/arcflash/getting_help/downloads/ICPS-wilkins011904_web.pdf
Original thread
http://www.arcflashforum.com/showthread.php?t=74
PostPosted: Fri Mar 18, 2011 3:04 am
Original thread
Hi Mike,
Forgot about that post. Good info!
Thanks!