It is currently Wed Nov 18, 2026 8:06 pm



Post new topic Reply to topic
Author Message
 Post subject: How do I submit a minor correction to IEEE 1584-2018?
PostPosted: Fri Sep 30, 2022 10:33 am 

Joined: Tue May 22, 2012 12:08 am
Posts: 30
I'm struggling to see how to submit a small typo to the IEEE. I did read that it should be possible to enter your comment at the bottom of the article on IEEE Xplore under "Comments". However, the IEEE Xplore page I'm looking at doesn't have a comments section.

The typo is in the coefficients listed in Annex D, Equation D.55. The k5 coefficient should be equal to 4.556*10^-10 (i.e. the third decimal place is missing).

It's hardly worth reporting on its own, but could be added to the existing Errata document.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: How do I submit a minor correction to IEEE 1584-2018?
PostPosted: Fri Sep 30, 2022 1:39 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
w5m wrote:
I'm struggling to see how to submit a small typo to the IEEE. I did read that it should be possible to enter your comment at the bottom of the article on IEEE Xplore under "Comments". However, the IEEE Xplore page I'm looking at doesn't have a comments section.

The typo is in the coefficients listed in Annex D, Equation D.55. The k5 coefficient should be equal to 4.556*10^-10 (i.e. the third decimal place is missing).

It's hardly worth reporting on its own, but could be added to the existing Errata document.


I keep an unofficial running list of items for the next edition which is not on the radar screen. I copied this thread into that list. Thanks!
Note: This is NOT an official confirmation of your submittal and is independent of IEEE (legal disclaimer)


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: How do I submit a minor correction to IEEE 1584-2018?
PostPosted: Tue Oct 04, 2022 1:27 am 

Joined: Tue May 22, 2012 12:08 am
Posts: 30
Many thanks Jim.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883