It is currently Wed Nov 18, 2026 8:38 pm
 Post subject: How do I submit a minor correction to IEEE 1584-2018?
PostPosted: Fri Sep 30, 2022 10:33 am
I'm struggling to see how to submit a small typo to the IEEE. I did read that it should be possible to enter your comment at the bottom of the article on IEEE Xplore under "Comments". However, the IEEE Xplore page I'm looking at doesn't have a comments section.
The typo is in the coefficients listed in Annex D, Equation D.55. The k5 coefficient should be equal to 4.556*10^-10 (i.e. the third decimal place is missing).
It's hardly worth reporting on its own, but could be added to the existing Errata document.
 Post subject: Re: How do I submit a minor correction to IEEE 1584-2018?
PostPosted: Fri Sep 30, 2022 1:39 pm
I keep an unofficial running list of items for the next edition which is not on the radar screen. I copied this thread into that list. Thanks!
Note: This is NOT an official confirmation of your submittal and is independent of IEEE (legal disclaimer)
PostPosted: Tue Oct 04, 2022 1:27 am
Many thanks Jim.