It is currently Sat Sep 26, 2026 7:36 pm
 Post subject: AF Technical Reports
PostPosted: Thu Apr 05, 2012 10:48 am
What do you guys use as a standard or outline on what to include in an AFS report?
PostPosted: Thu Apr 05, 2012 1:19 pm
Are you asking what to put on an RFQ?
PostPosted: Mon Apr 09, 2012 5:12 am
Not necessarily, just wondering what the industry standard is to provide a client when producing a written report with TCC curves/1 lines/ etc..
PostPosted: Mon Apr 09, 2012 6:59 am
our typical reports include:
Executive summary
report - describing findings - very detailed
Appdendixes
input data
arc flash data (study options and output)
onelines (input and arc flash)
TCC's as required (mitigation, cat 4 and dangerous) unless coordination is required
PostPosted: Mon Apr 09, 2012 9:58 am
whether we perform the studies or have them performed as part of an install contract, we typically include the below listed items. since we're an owner instead of a 1x engineering firm, we rely on current and past studies to update our systems and models, so some of the below info might be too extensive to include in a typical report.
what engrick said above, plus:
PE of record's license information and resume
the .dez file (EasyPower(EP)) or the copy of whomever's software you would use
utility data, and their point of contact
one-line diagram with load flow, power flow, short circuit, transient motor starting, harmonics if there are substantial numbers of drives, etc.
OCPD schedules, ratings, settings, etc.
system and load info: MCC and panelboard schedules
conductor and conduit schedules printed out from EP
source scenarios: standby generators, tie-breakers, UPSes, etc.
DC-system modeling
lastly, PDF copies of the labels they'll be filling out and afixing to the equipment.