 Post subject: Arc Flash Labels at WalMart!
PostPosted: Tue Dec 02, 2014 9:56 am
:o Well imagine my surprise when I saw this on WalMart's website: http://www.walmart.com/ip/BRADY-121108- ... 7/41376914
I can only imagine where this might lead to: "Why do I need a study when I can go to WalMart and buy labels?" or "Send me just the report and I will buy the labels at WalMart."
 Post subject: Re: Arc Flash Labels at WalMart!
PostPosted: Tue Dec 02, 2014 2:24 pm
Wow!
Next up: Craig's List and E-Bay!
Interesting that Category 1 is "Danger" and it is for operating controls.
PostPosted: Thu Dec 04, 2014 11:29 am
Don't like 1? How about 0? Wallmart (and Brady) has the answer:
http://www.walmart.com/ip/BRADY-121106-Appropriate-PPE-Required-Hazard-Category-0-Arc-Flash-Label/40875743
PostPosted: Mon Dec 08, 2014 8:40 am
Interesting choice. I guess if you are using the tables for your arc flash study (calculated short circuit and clearing time) you might be ok. This is another way to misuse the tables by not knowing the short circuit current and clearing time. If you are doing an incident energy analysis then you must identify the arc flash boundary and the incident energy, followed up with the risk assessment before determining PPE requirements.
PostPosted: Tue Dec 09, 2014 8:14 am
This is very concerning for the safety of working personnel and general public. Hope no one bought it. May be OSHA should get there ask for detail study report.
PostPosted: Thu Dec 11, 2014 6:14 pm
Walmart?? I anticipate that I should start checking Walmart stores up here in Canada! You know what they say whatever happens in the US, eventually comes here :)