It is currently Sat Oct 10, 2026 12:32 pm
 Post subject: Transmission Line Assumptions
PostPosted: Tue Jan 27, 2009 4:40 pm
I have been asked to calculate values for our 115 kV and 69 kV transmission lines. If anyone else is /has done this:
(1) What are you using for arc gap values?
(2) What are you using for typical working distances?
I'm looking for a sanity check on some numbers floating around in-house before I begin.
Thanks.
PostPosted: Mon Feb 09, 2009 12:27 pm
For our transmission lines I have used:
1) Arc gap - the vertical length of the insulator string (8 bells x 146mm = 1168mm or 46")
2) Working distance - MAID - minimum air insulation distance. That is the minimum approach distance minus the ergonomic safety factor. If an arc was generated there is a good chance that the ergonomic safety factor was breached.
However I haven't done the actual calculations yet due to the lack of a high voltage open air arc model. What arc model are you using to calculate incident energies?
PostPosted: Mon Feb 09, 2009 1:31 pm
Thanks.
NESC Table 410-2 uses an arc gap (in) = Ø-grd voltage (kV) divided by 10, on the basis of the dielectric strength of air being 10 kV per inch.
Working distance in Table 410-2 is calculated by using the minimum approach distance from Table 441-2 and subtracting two times the arc gap length. This would be 3'-11" for 69 kV and 4'-6" for 115 kV unless a maximum overvoltage other than 3.0 has been determined by engineering analysis.
PostPosted: Mon Feb 09, 2009 4:29 pm
Big difference. Table 2 suggests that a worker brings a grounded metal object within the air break down distance, holds it there for the duration, and the arc does not lengthen on its own. But using the insulator string strike distance can yield some pretty large incident energy values.
PostPosted: Mon Feb 09, 2009 9:33 pm
I just noticed that I added two times the arc gap length instead of subtracting. I'll have to look at this again in the morning, but off-hand it appears that this may yield smaller working distances for 115 kV than for 69 kV!
PostPosted: Tue Feb 10, 2009 10:32 am
I was right, the calculation of working distance according to the footnotes to NESC Table 410-2 result in a working distance for 69 kV of 2'-7" but a working distance for 115 kV of 2'-3". Doesn't seem to make sense having a shorter working distance at 115 kV than at 69 kV.
PostPosted: Thu Feb 26, 2009 9:14 am
table 441-2 needed
Could anybody post a copy of table 441-2 from nesc c2 in pdf or doc formats?
PostPosted: Fri Feb 27, 2009 5:44 pm
Transmission Arc Flash Model
I think the only model to consider is the ArcPro model, but I have several reservations about that one. I'm just trying to do some due diligence before I have to tell my boss "I can't do that".
PostPosted: Thu Jun 04, 2009 9:20 am
jghrist Error?
jghrist: I believe that you have used the Phase to ground voltage from table 441-1 (69kV=3' 3"). This distance should be 3' 11" from the phase to phase column for distance to employee. Subtracting 8" would give you 3' 3", not 2' 7".
Please confirm.... and repost. I think that you are ok for the 115kV line however. I do get 2' 3".
PostPosted: Thu Jun 04, 2009 9:33 am
Why use the value for Ø-Ø work in Table 441-1? If you used the Ø-Ø Table 441-3 for 115 kV, you would subtract 13" from 4"-7" and get 3'-6".