Post subject: Arc Flash Incident in Los Alamos Posted: Tue May 05, 2015 8:05 am |
| Top |
A2003
Post subject: Re: Arc Flash Incident in Los Alamos Posted: Thu May 07, 2015 8:50 am |
Photo The accident occurred during preventive maintenance operations at the facility. The employee was burned while working on an electrical substation.
| Attachments: |
| Top |
jmparks
Post subject: Re: Arc Flash Incident in Los Alamos Posted: Mon May 11, 2015 8:22 am |
A ladder is located in the cubicle. Was the injured worker using the ladder? Was the substation energized while maintenance work was being performed? Did the worker have proper PPE? Had an arc flash study been performed? Many federal agencies are way behind in electrical safety especially in the proper use of PPE.
| Top |
Oly
Post subject: Re: Arc Flash Incident in Los Alamos Posted: Mon May 11, 2015 9:13 am |
Where does it state that the photo from A2003 is directly related to the Los Alamos incident?? So many suppositions, so few facts.
| Top |
Hurwitz
Post subject: Re: Arc Flash Incident in Los Alamos Posted: Tue May 12, 2015 9:15 am |
Joined: Fri Aug 26, 2011 7:38 am Posts: 32 Location: Baltimore, MD