 Post subject: Size of Generator
PostPosted: Sun May 17, 2015 12:58 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1736
Location: Scottsdale, Arizona
When performing an arc flash study, consideration should be given to modeling different scenarios which may include operating from on-site generation.
This weeks' question:

What size of generator(s) does your company/clients have?

None
Less than 300kW/375kVA
301 to 2000kW/2500kVA
Larger than 2000kW/2500kVA


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Size of Generator
PostPosted: Mon May 18, 2015 8:28 am 
Sparks Level

Joined: Mon Jun 07, 2010 9:40 am
Posts: 119
That is a question that doesn't work well in a survey, with only a single answer allowed.
I have clients with no generation, small generators, all sizes of cogeneration, and several with paralleled generation (8eight 2000 kW units, with up to 7 paralleled at a time), I have clients with nothing but generation, that have no generators (They are PV systems ) and clients with nothing BUT wind generators.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Size of Generator
PostPosted: Mon May 18, 2015 8:52 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1736
Location: Scottsdale, Arizona
JKlessig wrote:
That is a question that doesn't work well in a survey, with only a single answer allowed.
I have clients with no generation, small generators, all sizes of cogeneration, and several with paralleled generation (8eight 2000 kW units, with up to 7 paralleled at a time), I have clients with nothing but generation, that have no generators (They are PV systems ) and clients with nothing BUT wind generators.


That is a great point JKlessig. Thanks for bringing it up. For those that have responses that don't line up with the limited choices of this survey, feel free to post your response instead.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Size of Generator
PostPosted: Thu May 21, 2015 11:21 am 

Joined: Thu May 21, 2015 11:07 am
Posts: 1
With 6 @ 2 MW generators in parallel, the actual number on-line depends on the load management system. A light load could possibly require only 3 generators. This means we don't have a lot of fault current available. Result = longer clearing times, sometimes very high IE. Do we need AF labels for normal operation & emergency operation?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Size of Generator
PostPosted: Mon May 25, 2015 8:32 am 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
gerald inzer wrote:
With 6 @ 2 MW generators in parallel, the actual number on-line depends on the load management system. A light load could possibly require only 3 generators. This means we don't have a lot of fault current available. Result = longer clearing times, sometimes very high IE. Do we need AF labels for normal operation & emergency operation?


My opinion is that you need a policy regarding normal and emergency operation if not labels. At one facility I've worked at, there are alternate feeders and standby generator power available that are never used (very infrequently, to the point I have never seen it). The policy at that plant was not to work on power systems when served by alternate source, and labels were only installed with calc's utilizing normal source.

This decision was not made to simplify the calculation only, but included consideration for the alternate source results being very different; resulting in labels that would not have served maintenance purposes.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883