It is currently Wed Oct 07, 2026 11:01 am
What is the largest calculated incident energy that you have seen?
Less than 50 cal/cm2 5%  5%  [ 2 ]
50 to 100 cal/cal2 21%  21%  [ 9 ]
100 to 250 cal/cm2 44%  44%  [ 19 ]
Greater than 250 cal/cm2 30%  30%  [ 13 ]
Total votes : 43
 Post subject: Largest Incident Energy
PostPosted: Sun Jun 05, 2022 3:43 pm
As a follow up to the last question regarding the largest Arc Flash Boundary, this question is about the largest Incident Energy.
50 to 100 cal/cal2
100 to 250 cal/cm2
 Post subject: Re: Largest Incident Energy
PostPosted: Sun Jun 05, 2022 4:20 pm
I saw a label years ago that was a bit above 1000 cal/cm2. Probably a case of "well that's what the software calculated" instead of knowing enough to question the result.
PostPosted: Sat Jun 11, 2022 5:59 am
I reviewed a report done by a firm for a company we were hired to do arc flash training for. They had a value of over 12,000 cal/cm^2 in a 115kV switchyard. I pointed out that this was absurd and that the wrong method had been used and that they had the working distance at 18 inches.