Hi all,
I would like to have your view regarding external grid short circuit scenarios in Arc Flash calculations. I have some doubts about how this issue should be addressed.
What should I do if there is no info about the available short circuit power in the grid?
As far as I understand, considering only hypothetical maximum and minimum short circuit scenarios for calculation I may not be achieving the “Worst Case” incident energy scenario. The reason is that there may be some intermediate Scc scenarios in which the combination of FCT + Icc may lead to a higher Incident Energy. So the correct approach may be doing a sweep with different values. There is also some scientific literature with conclusions pointing in the same direction.
Similar happens when the utility gives you the data: what about short circuit intermediate scenarios?
How do you see it?
Thanks for your support.
Regards,
| Top |
Tesla13
Post subject: Re: Grid short circuit data Posted: Fri Jun 30, 2023 12:56 am |
| Top |
mpparent
Post subject: Re: Grid short circuit data Posted: Fri Jun 30, 2023 6:50 am |
I think Jim has an article somewhere about this topic.