| Author |
Message |
|
jsoar
|
Post subject: How to model a Fused circuit breaker in SKM Posted: Tue Aug 13, 2024 8:13 am |
|
Joined: Wed Jun 12, 2024 5:19 am Posts: 35
|
|
Hello, How do I model a Fused circuit breaker in SKM? The breaker is 800A Cutler-Hammer DSL-206.
| Attachments: |

DSL206.png [ 93.04 KiB | Viewed 69219 times ]
|
|
|
| Top |
|
 |
|
bbaumer
|
Post subject: Re: How to model a Fused circuit breaker in SKM Posted: Tue Aug 13, 2024 3:19 pm |
|
| Arc Level |
 |
Joined: Fri Jul 08, 2016 10:01 am Posts: 488 Location: Indiana
|
Looks like you have an Eaton Magnum DS with current limiters. Just put the breaker and current limiting fuses in series with each other. Here is an example but I don't know exactly which breaker you have or what the amp rating is of the limiter so I just somewhat randomly picked them. This is in SKM. Attachment:
MDSL.jpg [ 398.84 KiB | Viewed 69216 times ]
Attachment:
DLS TCC.jpg [ 508.12 KiB | Viewed 69216 times ]
_________________ SKM jockey for hire PE in 17 states
|
|
| Top |
|
 |
|
jsoar
|
Post subject: Re: How to model a Fused circuit breaker in SKM Posted: Tue Aug 13, 2024 6:47 pm |
|
Joined: Wed Jun 12, 2024 5:19 am Posts: 35
|
|
Man, I think I have modeled it incorrectly. I thought it was fuse then breaker.
| Attachments: |
File comment: Another example for cb 6

IMG_0955.png [ 186.16 KiB | Viewed 69211 times ]
|
File comment: It's cb 6, 7, & the main circuit breaker.

IMG_0954.png [ 236.44 KiB | Viewed 69211 times ]
|
|
|
| Top |
|
 |
|
bbaumer
|
Post subject: Re: How to model a Fused circuit breaker in SKM Posted: Tue Aug 13, 2024 11:07 pm |
|
| Arc Level |
 |
Joined: Fri Jul 08, 2016 10:01 am Posts: 488 Location: Indiana
|
|
Not sure why it would make any difference. I have a customer with this type of gear and have the shop drawings with factory one-lines I can check but not until Thursday.
You might be right. I can't remember if it's breaker then fuse or fuse then breaker. Again though, makes no difference for anything downstream.
_________________ SKM jockey for hire PE in 17 states
|
|
| Top |
|
 |
|
bbaumer
|
Post subject: Re: How to model a Fused circuit breaker in SKM Posted: Tue Aug 13, 2024 11:24 pm |
|
| Arc Level |
 |
Joined: Fri Jul 08, 2016 10:01 am Posts: 488 Location: Indiana
|
Looks like you probably are correct fuse then breaker if I'm seeing this pic correctly. Attachment:
Screenshot_20240814-022259_eBay.jpg [ 600.05 KiB | Viewed 69206 times ]
_________________ SKM jockey for hire PE in 17 states
|
|
| Top |
|
 |
|
bbaumer
|
Post subject: Re: How to model a Fused circuit breaker in SKM Posted: Wed Aug 14, 2024 1:32 pm |
|
| Arc Level |
 |
Joined: Fri Jul 08, 2016 10:01 am Posts: 488 Location: Indiana
|
Bus then limiter then breaker according to some old shops I had. You were correct: Attachment:
MDSL Limiter Shops 1.jpg [ 86.43 KiB | Viewed 69201 times ]