It is currently Sat May 30, 2026 2:18 am
 Post subject: Would a Energized Work Permit Be Required??
PostPosted: Thu Jun 05, 2025 9:31 am
Scenario:
Troubleshooting a 120-volt circuit on a VFD. The task involves placing a jumper on energized male pins on the circuit board. The jumpers used are manufacture provided and are insulated (not alligator clips).
Would this task require an energized work permit? The technician is interacting with a energized component but would the jumpers be considered the same as a meter lead and thus not require a permit?
 Post subject: Re: Would a Energized Work Permit Be Required??
PostPosted: Thu Jun 05, 2025 9:40 am
Not enough information to provide an opinion.
Mike
PostPosted: Fri Jun 06, 2025 6:01 am
Mike
Help me out here, what more do you need?
PostPosted: Fri Jun 06, 2025 11:10 am
Just so happens Rozel/Guidant have a new article out related to this topic. Just got in email yesterday.
https://www.guidantpower.com/post/elect ... and-208vac
SKM jockey for hire
PE in 17 states
PostPosted: Fri Jun 06, 2025 12:18 pm
That article gives a lot of good information around the hazards but my question is more around the need for a work permit. 70E 130.2(C)(1) list testing and troubleshooting as an exception to the work permit. In my scenario would installing the jumper be considered troubleshooting or is that considered working on energized equipment as defined in 70E?
PostPosted: Sun Jun 08, 2025 8:03 am
I believe a factory insulated jumper is part of the troubleshooting process. But, this is also one of the reasons Energized Work Permits should exist.
This is purposely a gray are in NFPA70E. It is up to each company to develop and implement their own safety rules, based on their procedures. A qualified person should be able to analyze the risk associated with these jumpers.
It can be a problem keeping a production line working when companies issue a blanket No Energized work EVER policy.
PostPosted: Tue Jun 10, 2025 8:00 am
Yes, but having a plant manager need to sign a permit for this task seems a bit over the top, especially when troubleshooting a VFD at 2 AM. I agree the wording in 70E is gray in places and in my opinion that can lead to broad interpretations of the standard. The problem with leaving it to a qualified person to decide is if something happens, the first thing that will be asked is did you have your energized work permit because you are interacting with an energized component.
PostPosted: Tue Jun 10, 2025 8:36 am
Sorry, not more help here but what you are describing seems to be about as dangerous as plugging in a desk lamp unless where the jumper is located is adjacent to exposed 480V live parts.
SKM jockey for hire
PE in 17 states
PostPosted: Tue Jun 10, 2025 11:46 am
Thanks Brent...that's exactly why I responded to the OP as "more info needed."
Mike
PostPosted: Thu Jun 12, 2025 6:07 pm
Win Engineer wrote:
Yes, but having a plant manager need to sign a permit for this task seems a bit over the top, especially when troubleshooting a VFD at 2 AM. I agree the wording in 70E is gray in places and in my opinion that can lead to broad interpretations of the standard. The problem with leaving it to a qualified person to decide is if something happens....
Part of being qualified is knowing your company's policies/requirements. What restrictions does your Electrical Safe Work Practices program use to determine troubleshooting versus energized work? NFPA70E does not answer this question for you.
I wish companies would put thought into their ESWP and update them regularly, at least every time there is a new edition of 70E.