 Post subject: NEC 240.21(C)(1) Transformer Secondary Conductors
PostPosted: Wed Sep 17, 2025 6:42 am 

Joined: Tue Jun 14, 2022 11:35 am
Posts: 28
I'm curious how long has this been in the NEC? The reason I ask is because I am currently working on a project for a major company and the facility I am in (large industrial manufacturing site) probably has close to 100 208-volt panels fed from 480V/208V wye transformers and very few have main breakers in the panels or any other form of secondary protection. The facility is old with most equipment being installed in the late 1960's to early 1970's. Was this around back in that time frame? I find it hard to believe that this client would have built a plant with their engineering expertise that was not to code, but it certainly would not be to standard today.


240.21(C)(1) Protection by Primary Overcurrent Device. Conductors
supplied by the secondary side of a single-phase transformer
having a 2-wire (single-voltage) secondary, or a three-phase,
delta-delta connected transformer having a 3-wire (single-voltage)
secondary, shall be permitted to be protected by over‐
current protection provided on the primary (supply) side of
the transformer, provided this protection is in accordance with
450.3 and does not exceed the value determined by multiplying
the secondary conductor ampacity by the secondary-to-primary
transformer voltage ratio.
Single-phase (other than 2-wire) and multiphase (other than
delta-delta, 3-wire) transformer secondary conductors are not
considered to be protected by the primary overcurrent protec‐
tive device.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NEC 240.21(C)(1) Transformer Secondary Conductors
PostPosted: Wed Sep 17, 2025 6:50 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 438
Location: Indiana
I don't have time to look through old versions of the NEC right now but if you like, you can look it up via the NFPA free access site or Google.

https://www.nfpa.org/codes-and-standard ... lopment/70

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NEC 240.21(C)(1) Transformer Secondary Conductors
PostPosted: Wed Sep 17, 2025 7:53 am 

Joined: Tue Jun 14, 2022 11:35 am
Posts: 28
bbaumer wrote:
I don't have time to look through old versions of the NEC right now but if you like, you can look it up via the NFPA free access site or Google.

https://www.nfpa.org/codes-and-standard ... lopment/70


Thanks for the link. It appears that between 1996 and 1999 they made some changes to the wording in that section.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NEC 240.21(C)(1) Transformer Secondary Conductors
PostPosted: Fri Sep 19, 2025 2:32 am 

Joined: Mon May 25, 2020 6:30 am
Posts: 3
when a panelboard is supplied through a transformer, the OCPD is required on the secondary of the transformer per NEC 408.36(B) unless the secondary side is protected by the OCPD on the primary side per 240.21 (C) (1)


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: NEC 240.21(C)(1) Transformer Secondary Conductors
PostPosted: Sun Sep 21, 2025 2:47 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 601
Location: Wisconsin
Win Engineer wrote:
bbaumer wrote:
I don't have time to look through old versions of the NEC right now but if you like, you can look it up via the NFPA free access site or Google.

https://www.nfpa.org/codes-and-standard ... lopment/70


Thanks for the link. It appears that between 1996 and 1999 they made some changes to the wording in that section.


Yes.
Prior to the 90s it was common for transformer secondary conductors to not have a single OCPD when feeding panelboards.
Part of this had to due with the NEC and its requirements the Lighting and Branch Circuit Panels to have a main breaker while Power Panels did not need one.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883