 Post subject: Fused Disconnect Modeling
PostPosted: Thu Jan 29, 2026 1:28 pm 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 9
I am currently on a site that has a disconnect with 3 different fuses inside. How would you model this?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Fused Disconnect Modeling
PostPosted: Thu Jan 29, 2026 5:09 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 463
Location: Indiana
Got a pic? Like 3 different brands but same amp and type or 3 different types or 3 different amp ratings or some combination of the above?

For example, (from memory) Buss Frs-R-100, Gould trs100r and Littelfuse FLSR100? All are the same curve. Pick one.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Fused Disconnect Modeling
PostPosted: Fri Jan 30, 2026 3:50 am 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 9
I modeled them below. All 50A, curves are slightly different


Attachments:
Screenshot 2026-01-30 054720.png
Screenshot 2026-01-30 054720.png [ 27.33 KiB | Viewed 16 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Fused Disconnect Modeling
PostPosted: Fri Jan 30, 2026 6:49 am 

Joined: Tue Jun 14, 2022 11:35 am
Posts: 30
As long as they are all RK5 fuses with the proper voltage rating, I generally just pick one and put a note on the drawing that the switch has fuses from different manufactures. If you have RK5 and RK1 fuses in the same switch I will model with the RK5.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Fused Disconnect Modeling
PostPosted: Fri Jan 30, 2026 8:41 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 463
Location: Indiana
Win Engineer wrote:
As long as they are all RK5 fuses with the proper voltage rating, I generally just pick one and put a note on the drawing that the switch has fuses from different manufactures. If you have RK5 and RK1 fuses in the same switch I will model with the RK5.


This. ^^^^^^

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883